A classroom has 15 m² of glazing. The existing glazing has a U-value of 5.0 W/m²K, while a proposed double-glazing system has a U-value of 2.0 W/m²K. The indoor design temperature is 22°C, and the outdoor winter design temperature is 6°C. Assume that all other sources of heat loss remain unchanged and can be ignored for this calculation. Calculate the reduction in heating load (in kW) resulting from the glazing upgrade. 数值题